What causes electrical outlets to just stop working?

House Repair Talk

Help Support House Repair Talk:

This site may earn a commission from merchant affiliate links, including eBay, Amazon, and others.

thealfa

Member
Joined
Jun 20, 2011
Messages
17
Reaction score
0
I've never worked on electrical stuff at home so I'm not sure what caused an electrical outlet to just stop working. It doesn't have a reset button either.

Also I've attached a picture of a light fixture that used to work just by pressing a button but it just stopped working. What caused it to stop working? I don't know how to open it up to see what's going on with it.
 

Attachments

  • 20241222_052316.jpg
    20241222_052316.jpg
    1.8 MB
  • 20241222_061919.jpg
    20241222_061919.jpg
    1.5 MB
What causes electrical outlets (receptacles) to stop working - there are many reasons why something like this can happen so the first thing we have to do is process of elimination so we can narrow down the causes.

Since you are very limited in residential electrical experience we can only offer just so many suggestions before you have to say "this is beyond my ability". It is ok to admit this when the time comes. It could be something very simple or it could be something complex.

Just like when you go to the doctor you can't just say you don't feel well and you expect the doctor to know what is wrong with you. You have to give as many symptoms as possible to narrow down the possible cause.

It doesn't have a reset button either.

There does not have to be a reset button on the receptacle itself. If this receptacle and light is on a circuit which is protected by a GFCI upstream this could cause the circuit after the GFCI receptacle not to work if the GFCI receptacle tripped (the GFCI receptacle if this is the problem does not even have to be in the same room).

Narrow down the possible cause:
#1 - Besides this light fixture and this receptacle you show in the pictures is there anything else so far that is not functioning?
#2 - Have you checked to see if a breaker tripped in the breaker panel? Do you know how to test/see if a breaker has tripped?
#3 - I would go to each GFCI receptacle in the entire house and press the "Test" button and then the "Reset" button on every one of them. Use the very tip of your finger to press firmly inward on these buttons. Yes, every one; does not matter it's location in the home compared to where this problem is located. This is what an electrician would do to start with along with making sure no breakers tripped in the panel.

Once you check these 3 things get back to us and let us know your findings. If you find any GFCIs that you can not reset make note of where they are located.
 
A few months ago, I was over at my niece's house for dinner. After we ate, I went to charge my phone but noticed one of the outlets wasn’t working. My niece mentioned that it had been acting up for a while, and they weren’t sure why. The first thing that came to mind was to check the breaker box. I got up, looked through the breakers, and sure enough, one of them had tripped. I flipped it off and back on, and the outlet started working again. It felt good to fix it without much hassle!

Later that evening, another little issue popped up. A small lamp next to the couch, the kind you turn on with a button, suddenly stopped working. My niece guessed the button might be broken. I took a closer look and noticed the lamp’s cover could be opened with a screwdriver. Once I got it open, I saw that one of the wires had come loose. I reattached it, and the lamp was back in business. That night taught me that small electrical problems often have simple fixes—provided you’re careful and follow safety basics!
 
I work industrial and distribution, but do the required Family And Friend house freebies. Very often in houses I find that receptacle outlets or switches stop working because "upstream" someone put two wires under one receptacle screw. Sooner or later, heating and cooling cycles will loosen the screw enough so that a wire comes off.

Also often found are receptacle outlets that are the spring loaded Push-In kind. The wire leaving to the next receptacle loosens and burns off. Those type I advise against- strongly.

Now What?
Assuming you don't know the path, with power off, start opening receptacle outlets and switches. Look for a Fall Off or a loose wire that is about to fall off.

If you think you know the path (or can guess), open the first in line that is not working and if that is not it, back up to one that is working to seek a fallen off wire leading to the first dead outlet.


I'd have to say that 90% of the friend calls for suddenly dead receptacle or light I fix are from one of the above. The other ten percent are from twist on wire connectors (Wire Nut is a brand of those) where a wire fell out or was nicked during stripping and eventually broke.

Happy Hunting!
Paul
 
Now What?
Assuming you don't know the path, with power off, start opening receptacle outlets and switches. Look for a Fall Off or a loose wire that is about to fall off.

If you think you know the path (or can guess), open the first in line that is not working and if that is not it, back up to one that is working to seek a fallen off wire leading to the first dead outlet.
I would suggest that before opening receptacle boxes and checking them that we make sure it is not a tripped GFCI or tripped breaker first. The OP does not have experience with residential electrical so this may be a bit too much too quick and may not even be necessary yet.

I suggest 1st to look for a tripped GFCI receptacle/outlet or breaker and let the OP come back with their findings and then take it from there.
 
I'm always helping friends with GFCI resetting. There is never a rhyme nor reason for where they are located.
 
I did check the gfci breaker panel and none was switched off. The receptacle outlet that isn't working is in the living room, yet other receptacle outlets in the living room works. So could the issue not be in the gfci breaker panel? The non working receptacle outlet does seem a bit unusually "tight" when I tried to charge my phone there to see if it's working. This receptacle outlet stopped working months ago, that's why I'm curious how to make it work again.

I've attached a picture of the gfci breaker panel located in the basement. I've switched off and then turned on the ones I think would fix the dead receptacle outlet. Still not working.
 

Attachments

  • 20241224_114819.jpg
    20241224_114819.jpg
    2.4 MB
Last edited:
You took a picture of your breaker panel. This is a ground fault circuit, so it will shut off when needed, completely independent of the circuit breaker.17351412016296369089183444635698.jpg
 
I did check the gfci breaker panel and none was switched off. The receptacle outlet that isn't working is in the living room, yet other receptacle outlets in the living room works. So could the issue not be in the gfci breaker panel? The non working receptacle outlet does seem a bit unusually "tight" when I tried to charge my phone there to see if it's working. This receptacle outlet stopped working months ago, that's why I'm curious how to make it work again.

I've attached a picture of the gfci breaker panel located in the basement. I've switched off and then turned on the ones I think would fix the dead receptacle outlet. Still not working.
You mentioned Living Room, Thealfa.
Please don't take any disrespect from this reply. It's offered with respect and as a suggestion for something that is often overlooked.

In living rooms, there is often a wall switch that controls a receptacle outlet or half of it. And sometimes the switch also controls a wall sconce or two. Usually the sconces have a push button on the fixture for individual control. (Popular in the 40's and 50's)

I've had several times people call me because a living room receptacle outlet suddenly does not work. So often it is simply a switch that got turned off. And, in my home someone whose name will not be mentioned (me) sometimes forgets and wonders why the table lamp won't turn on. A quick flip of the forgotten switch solves the mystery!

Maybe make sure the switches are on and, if you are comfortable working with electricity, that the switch is good.
Paul
 
In living rooms, there is often a wall switch that controls a receptacle outlet or half of it. And sometimes the switch also controls a wall sconce or two. Usually the sconces have a push button on the fixture for individual control. (Popular in the 40's and 50's)
Excellent point and something that can be overlooked quite easily by a home owner.

@thealfa PJB12 brought up a good point. You just may never had realized that a wall light switch controls this receptacle and wall sconce. Take a lamp or radio and plug it into one of the spots on the receptacle. Try flipping the light switches in the room. If the lamp/radio does not go on after flipping all of the switches in the room pull the plug out of the receptacle and place it in the other slots and do the same flipping all of the light switches in the room. It is possible that you just never noticed that a light switch controls the receptacle and wall sconce.

If the above, flipping all light switches in the room does not solve the issue then again, you need to test every GFCI receptacle in the house. Any receptacle with a "Test"/"Reset" button on them no matter where they are located in the house, the kitchen, garage, outdoors, basement, everywhere. Press the "test" button with the very tip of your finger and then the "reset" button on each GFCI in the house. It is possible that a GFCI receptacle may be protecting this downstream receptacle in your living room.

You refer to your breaker panel as a GFCI breaker panel. This is not correct terminology. It is a circuit breaker panel. A circuit breaker panel can have individual GFCI breakers in it. According to the picture of your panel you do not have any GFCI breakers in it. Are you sure you do not have any other breaker panels in the house, garage etc?

Sometimes when a breaker trips it is very difficult to tell just by looking at the breakers to see if a breaker has tripped. What I suggest you do is start at the first top left breaker, gently wiggle the breaker handle side to side and get used to how much play is in the breaker. Do not turn it on and off doing this. Then go to the top right and do the same thing to that breaker, repeat the same procedure on each and every breaker on the panel. You will find that they all have the same resistance when wiggling the breaker handles. If you find one that has far more "play" in it then push that breaker handle all the way to the "off" position (you will hear it click) and then back to the "on" position. This is the proper way to reset a breaker.

Report back after you have tried the above.
 
You just may never had realized that a wall light switch controls this receptacle and wall sconce. Take a lamp or radio and plug it into one of the spots on the receptacle. Try flipping the light switches in the room.
Or, if it is like my "Fun House" was, the switch might be in adjacent room. A hallway switch operated a receptacle outlet in the living room. A switch at the bottom of the stiars operated an outlet in a 2nd floor room.

Are you sure you do not have any other breaker panels in the house, garage etc?
The photo shows Circuts 38/40 for a sub panel. Gotta check that load center, too.

Sometimes when a breaker trips it is very difficult to tell just by looking at the breakers to see if a breaker has tripped. What I suggest you do is start at the first top left breaker, gently wiggle the breaker handle side to side and get used to how much play is in the breaker.
That's a very good point, Afjes_2016!
The new Eaton BR (as shown above) and the older Cutler Hammer BR will be obviously tripped with a short circuit, but not with an over-current trip. Same with the older ITE snap-ins.

With over-current trip, the handle is just wiggly-loose and looks at a glance to be still on. (Square D's older QO = Halfway handle for over-current trip and red flag with short circuit.)

Wise Idea-
At least once per year, cycle every circuit breaker from on to off to on. Do this twice a year if they are in a damp location such as outdoors or in an unconditioned area of a basement.
And don't forget to test GFI devices monthly.

Paul
 
Back
Top