I am adding a point of use water heater under my kitchen sink because it takes over a minute of running water to get hot water to the faucet. There is currently a pair of unused 12 ga white-black conductors wired to the main panel with a 20 amp breaker. There is a separate ground wire running to the dead-ended box where the unused circuit terminates. It was apparently intended for some future use, but is not pulled through a conduit, so I cannot replace it.
-> is it permissible by code and good practice to re-purpose the white conductor (painting it red in the main panel to indicate it is now a hot lead) to a 2nd pole breaker (installing a new two-pole breaker) and use it for the 2nd pole of a 220 v 20 amp circuit? That would increase the wattage I can support at the under-sink heater.
Is that question clear?
Thanks for your thoughts and comments.
Hello Dsteinhorn!
Above, JoeD mentioned recolouring the wire is OK for your use. I noticed his proper spelling of "colour" & guess Joe's not in the U.S. where we spell it wrong. Here's the U.S.'s NEC (NFPA 70) take on it:
As long as the conductors are
in a multi-conductor cable all the way, it's OK by NFPA 70 to do as you propose unless local code contradicts. If, at some point in the run, the cable switches to conduit with individual conductors, it's
Not allowed to change the color of the white # 12. (those rules change with wire size)
Don't ever re-color the bare ground. It's for grounding (earthing) only.
Make certain that any place the conductors are exposed are colored. Example: If there is a junction box along the way to the final destination & the jacket is stripped in the box. I suggest permanent marker or paint marker instead of tape which can fall off, confusing someone later.
Note that the rules differ a bit regarding re-coloring for 3 and 4-way switches. SEE NFPA 70 200.7 for that variously interpreted section.
Not That You Asked-
It's not my business & I hope you don't mind a suggestion, but 20 amps is a generous circuit. You may find a 120 volt point-of-use that will suffice for your needs. This will save you some money on circuit breaker & save you some time.
Also, people I know have installed point-of-use on the hot water line & asked why they get instant hot water, then a minute or so of cold, then hot again. Phas 1: Hot from the Instant heater Pahse 2: Cold from water that was dormant in the supply pipes. Phase 3: Hot from the water heater
Paul